• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Daycare Playground - Occupant Load Calculations

Papio Bldg Dept

Platinum Member
Joined
Jan 24, 2011
Messages
1,414
Location
Papillion
What would be an acceptable design occupant load calculation for a 1,820 square foot child daycare playground?

a) @ assembly standing space; 1/5 net ratio,

b) @ day care; 1/35 net ratio,

c) @ exercise rooms; 1/50 gross ratio, or,

d) determined by Owner/Tenant/RDP in signed/sealed letter of operations for maximum occupant load, and posted at entrances to playground (i.e., maximum occupant load of 49)?

Would these be considered an application of 1004.1.1, and it's exception for reduced design occupant load?
 
Outside????????

Inside???????

fenced in / outside where you have to exit back into the building??????????
 
cda said:
fenced in / outside where you have to exit back into the building??????????
Yes, the playground is a fenced in outdoor area (not under any roof projections), with two means of egress entering the area. No gates or sidewalks are provided for access to the public way from the playground area. Egress is back through the building. Area is not far enough from building to constitute an area of refuge (or whatever it is called in that code section).
 
I would probably pick 50

what is the occupant load of the day care itself???

and looks like you would want at least one gate, so they have a choice not to go back into the burning building

do they happen to have the children exit into the playground when they have fire drills???????????????
 
cda said:
I would probably pick 50what is the occupant load of the day care itself???

and looks like you would want at least one gate, so they have a choice not to go back into the burning building

do they happen to have the children exit into the playground when they have fire drills???????????????
1004.8 (2006 IBC) requires an egress from the outdoor area, but does not specifically say it can't be back through the burning building, so to speak, if it is an area used only by the occupants of the building. I believe it would be good to have a means of egress that doesn't go back through the building, but I don't believe I can require it. I agree I should probably set the occupant load at 50, and it appears it already would meet the two means of egress requirement (both back into the burning building again), with minor changes to door swing, etc.
 
well also, is some of the building exiting into the playground area???????????

with out seeing the entire set up the playground area might or should be part of the "E" and that alone might kick in two exits from the playground area, one into the building and one out of fenced area.
 
Possibly another way to look at it?

Based on the driving section to determine OL for the type of occupancy “Daycare” in T-1004.1.1 and the reference by 1004.1 to “accessory to primary” since there is no gate to public way. The calculation of 1820/35 = 52 without subtracting the fixed playground equipment to determine the net figure for the playground area. The figure of 50 should be a safe bet if using the exception of 1004.1.1…….IMHO
 