Section 1017 CORRIDORS IBC 2006 has requirements for dead ends, and 1017.3 specifically references "dead ends in corridors". Nowhere else do I find references to dead ends in exits, aisles or other. Am I to assume that if a building meets requirements for common path of egress and travel distance, and the exit is not in a corridor, that code is met? Specifically, I am dealing with a storage occupancy with aisles between racks that, as designed, have "dead ends" of up to 40 ft. It makes no sense to meet the 20 ft. limit shown in 1017, but 100 ft. (common path limit per 1014.3 exception 1: sprinklered) seems like a very long way.