Dedicated Laundry Circuit

jar546

CBO
Joined
Oct 16, 2009
Messages
12,994
Location
Not where I really want to be
Can the laundry light and fan be put on the laundry circuit?

210.11©(2) Laundry Branch Circuits. In addition to the number

of branch circuits required by other parts of this section, at

least one additional 20-ampere branch circuit shall be pro-

vided to supply the laundry receptacle outlet(s) required by

210.52(F). This circuit shall have no other outlets.
 
"supply the laundry receptacle outlet(s) required by

210.52(F). This circuit shall have no other outlets."

It specifically calls out receptacle outlets, fan and lights are outlets, but not receptacle, so I so no go.
 
fatboy said:
"supply the laundry receptacle outlet(s) required by210.52(F). This circuit shall have no other outlets."

It specifically calls out receptacle outlets, fan and lights are outlets, but not receptacle, so I so no go.
I agree. Other receptacles outlets are allowed but not lighting or fan outlets-- 210.52(F) references receptacle outlets
 
\ - / - \

If the light and fan circuit remain in the Laundry ONLY, then yes,

they can be on the same circuit......I have never seen a fan in

a Laundry, and I am assuming that Jeff meant a Bathroom fan

connected on the same circuit, which would be a definite "no no" !

\ - / - \
 
north star said:
\ - / - \If the light and fan circuit remain in the Laundry ONLY, then yes,

they can be on the same circuit......I have never seen a fan in

a Laundry, and I am assuming that Jeff meant a Bathroom fan

connected on the same circuit, which would be a definite "no no" !

\ - / - \
Not at all, I specifically meant fan and or light.
 
I have an exhaust fan in my laundry.........and it is not part of the receptacle outlet circuit...........
 