Demising wall fire rating

ELLEN09US

Member
Joined
Oct 31, 2014
Messages
140
Location
LOS ANGELES
Hello, all,

My TI is in a medical building. Does the demising wall should be 1 hour fire rated between the tenant (pharmacy) and the other tenant (medical facility)?
Thank you!
 
To answer this question, we will need substantially more information.

Construction type, building area, occupancy types (may be multiple) and their respective areas, sprinkled or not, other fire resistive elements (fire walls, barriers, etc.), etc.

Pretty much need a full code analysis before any of us should begin to render any answers. Plans are needed.
 
Code rarely "requires" a demising wall between tenants......Malls are about all I can think of....
Hmm...I am thinking that it may be a separation of use in a mixed us building.

Also, OP stated medical, so could be a smoke compartment issue. Or if its any protected (Type A) construction, then it may have a required fire resistance.
 