What IRC code would you cite?
(easy one)
(easy one)
That is what I usually see. Destroyed plates.jar546 said:What are these guys thinking. Just make swiss cheese and pull 2 per hole.
In the 2008 NEC you are required to adjust the ampacity of NM cables in accordance with 310.15(B)(2)(a). (See 334.80)GHRoberts said:jar546 ---I don't want to pick on you but ...
The holes are not that bad. I would like to see them further apart, but it does not seem to be a big issue.
There is no need to derate the cables. More than 24" seems to be the "conduit" length that requires derating.
Don't do electrical so where's the foam in the top plate penetrationsWhat IRC code would you cite?(easy one)
I don't do a lot of electrical work, but my understanding is:raider1 said:In the 2008 NEC you are required to adjust the ampacity of NM cables in accordance with 310.15(B)(2)(a). (See 334.80)Under the 2005 NEC there was a loop hole that permitted you to not adjust the ampacity if the cables were not bundled for more than 10% or 10 feet. (See 310.15(A)(2) Exception). In the 2008 NEC 334.80 was change to state that the exception to 310.15(A)(2) would not apply to cables bundled through a firestopped framing member.
Chris
Let me post the wording of 334.80.There is no fire stopping shown. The cables are not bundled.
This section say "through the same opening in wood framing that is to be fire or draft stopped using thermal insulation, caulk, or sealing foam."Where more than two NM cables containing two or more current-carrying conductors are installed, without maintaining spacing between the cables, through the same opening in wood framing that is to be fire- or draft-stopped using thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a) and the provisions of 310.15(A)(2), Exception, shall not apply.
I agree, if it is required to be firestopped.raider1 said:So IMHO the picture shows cables that run through the same opening and the building code do require that the holes in the top plate be draft stopped so adjustment of the allowable ampacity needs to be done.
Chris
I agree, if it is required to be firestopped.TimNY said:raider1 said:So IMHO the picture shows cables that run through the same opening and the building code do require that the holes in the top plate be draft stopped so adjustment of the allowable ampacity needs to be done.
Chris
ChrisR302.11 Fireblocking. In combustible construction,fireblocking shall be provided to cut off all concealed draft
openings (both vertical and horizontal) and to form an effective
fire barrier between stories, and between a top story and the
roof space.
Fireblocking shall be provided in wood-frame construction
in the following locations:
4. At openings around vents, pipes, ducts, cables and wires
at ceiling and floor level, with an approved material to
resist the free passage of flame and products of combustion.
The material filling this annular space shall not be
required to meet the ASTM E 136 requirements.
The pictures do not show this as a concealed area. (Perhaps jarXXX can clarify this point.)fireblocking shall be provided to cut off all concealed draft openings.
Two of the holes appear to have 10 current carrying conductors, one appears to have 12, and one 14.TCN said:...there would have to be nine current carrying conductors before any further derating is required...
jar,It is a garage wall that will be sheetrocked as there is a bonus room above. You are looking at the inside of the exterior garage wall that will be behind the bonus room kneewalls.
[/size][/b]north star said:TimNY,
The drilled holes WILL be concealed once the sheetrock is installed, so R602.8, #4 would apply.
It is a garage wall that will be sheetrocked as there is a bonus room above. You are looking at the inside of the exterior garage wall that will be behind the bonus room kneewalls.
I agree with you.. The point was that I believe there are differing opinions as to whether or not you have to firestop the hole if it is not concealed. We were not originally privy to the location of the penetrations, and the location made a difference to some, and not to others.TimNY said:It being a concealed location per jar's explanation, I think we're in agreement that it violated the NEC.
Chris and I got a bit off topic, apologies. I tried to be clear.TimNY said:My interpretation would be that since it is not concealed [in my theoretical scenario, not in this particular photo]