How do you derate NM cable that is bundled for more than 24"? The chart only shows conductors, not cables. Are we supposed to be counting all of the conductors in all of the cables?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
We do….can’t remember if we have an amendment or common sense…How do you derate NM cable that is bundled for more than 24"? The chart only shows conductors, not cables. Are we supposed to be counting all of the conductors in all of the cables?
So that gets adjusted off of the 90 degree column?On 12/2 or 14/2, you count the nuetral and the hot, but not the ground wire because it is not current carrying. That means two conductors per cable. If you have 12/3 or 14/3, the neutral doesn't count either because it only carries unbalanced load from the two hots, so you only count the two hot wires - meaning that you still have two conductors per cable.
The TL;DR is that if you have more than 4 cables bundled of 14/2, 14/3, 12/2, or 12/3, you will have eight current carrying conductors, and that will be a bundling violation unless you do something unorthodox with your overcurrent protection.
9 CCC was what was sticking in my head…The derating factor is based on the ampacity in NEC Table 310.16. This may be higher than the breaker rating if the insulation is rated over 60° C. You can have (6) #14 75° C conductors or (9) 90°C conductors and still use a 15 A breaker.
Yes. You adjust the ampacity based on the value in the 90 degree column as you are allowed to do per 334.80. If the resulting number will still work with a breaker sized off the 60 degree column, you are good.So that gets adjusted off of the 90 degree column?
That's true if your 12/3 or 14/3 is carrying an MWBC, or if two of the conductors are travelers in a lighting circuit (per the footnote to Table 310.15(C)(1)). But if you had, say, a neutral, a constant hot, and a switched hot, then that counts as 3 CCCs. [Even if both hots are protected by the same breaker, which is a flaw in the NEC that for some reason the NFPA did not want to rectify when I proposed a change in the footnote to Table 310.15(C)(1).]If you have 12/3 or 14/3, the neutral doesn't count either because it only carries unbalanced load from the two hots, so you only count the two hot wires - meaning that you still have two conductors per cable.
NM-B cable is required to have 90C rated insulation, so when derating modern NM cable, you can always use the 90C column as your starting point.The derating factor is based on the ampacity in NEC Table 310.16. This may be higher than the breaker rating if the insulation is rated over 60° C.
Not necessarily. It's a violation if the circuit is supplying more than one receptacle for cord-and-plug connected portable loads. If it is not, then 240.4(B) applies, and it's fine to protect 12.5A ampacity conductors at 15A.Since the 12.5 amps of capacity we calculated is less than the 15 amps in the 60 degree column, it would be a violation to put 5 bundled 14/2 NM cables on a 15 amp or larger breaker
I think the wording is pretty clear. If the branch circuit supplies more than one receptacle for portable cord and plug connected loads, you may not use 240.4(B). If it does not, it passes 240.4(B)(1) and you may proceed to check the remaining requirements. Note that multiple cord and plug connected fixed-in-place loads are fine, only receptacles for portable loads are an issue.There is two ways to interpret (1). It could be assumed that a conductor could not supply a branch circuit with more that one receptacle.
Hold it up to a mirror. The wording is clear to both trains of thought. The arcane premise that multiple receptacles that are open to use by portable loads is somehow a greater concern than a load of unknown description raises questions.... as in perhaps that's not where they went with this.I think the wording is pretty clear.
Not following--the "portable cord-and-plug connected loads" are the unknown loads. Any fixed-in-place cord-and-plug connected loads, or hardwired loads, are known and need to be reflected in the Article 220 load calculation, and hence 210.19(A)(1)(b) requires they not overload the circuit. It is the unknown portable cord-and-plug connected loads that are a potential issue.The arcane premise that multiple receptacles that are open to use by portable loads is somehow a greater concern than a load of unknown description raises questions.... as in perhaps that's not where they went with this.