• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Determination of Occupant Load for an Existing 1 storey building.

Occupant load of existing buildling by dividing aggregate door width by 6.11 mm/person?

  • Yes

    Votes: 0 0.0%
  • No

    Votes: 1 100.0%

  • Total voters
    1

Zef Pepaj

Registered User
Joined
Jan 24, 2020
Messages
3
Location
Toronto, ON.
Hello all,

I have been tasked with letting the client know if they can remove a fire alarm system which has not been in operation for quite some time. The building is a one storey restaurant with exits leading to the outside. I have yet to go to site and measure the building floor areas.

In preparation for my site visit, I am trying to come to an understanding in what exactly to look for on site. If the building is sprinklered, the fire alarm system will remain in order to provide for the remote monitoring of the sprinkler system supervisory and alarm conditions.

I know that the threshold for requirements for a fire alarm system in a restaurant is 150 persons. As per 3.2.4.1. (2) (g) of the O.B.C.

The O.F.C. states that the occupant load shall be the lower of the occupant loads as indicated in:
-The OFC 2.7.1.4 (3) to 2.7.1.4. (7) or the occupant load for which the means of egress are provided as determined by the O.B.C.

I already understand how to determine the occupant load using the O.F.C. requirements. My issue is with figuring out the occupant load based on the O.B.C requirements.

My question is this:
Can I calculate the occupant load of an existing building under the O.B.C. by simply going to site, measuring the width of all exit door exits. Once I have the aggregate exit width, divide it by 6.11 mm per person?

My understanding is that occupant load is used (in the O.B.C.) to determine exit width and number of exits for a building when it is in the design phase (along with various other code requirements that are driven by occupant load). So if that is the methodology in determining occupant load for designing a building, can I just work backwards and divide the aggregate door width by 6.11 mm to determine the designed occupant load.

I appreciate any and all responses.

Much Regards,
 
Working backwards, as you have suggested, will grossly over estimate the occupant load.

I see doors every day that have calculated egress widths less then 1-ft, but are provided with multiple 3-ft doors. Your proposed method will certainly raise the occupant load to an exceedingly high number.

Instead, have you reached out to the local AHJ and requested a copy of the Certificate of Occupancy? It would be noted therein.
 
Occupant load is based on available floor space of the tenant - The older Southern Building Code Congress used to allow us to post Occupant Content based upon means of egress provided........ the allowable number of people based upon egress width.


However, I would prefer a multi-faceted look at the area being used - also include occupant
load as allowed by public restrooms provided - often or not, this usually is the limiting factor
for occupant loads for dining places.
 