Direct Vent in bedroom

Depends....Need more info

Section M1502.1 IRC 2009, Section 504.6 IMC 2009 .... heaters located in a bedroom or bathroom shall be installed in a sealed enclosure
 
2010 CALIFORNIA MECHANICAL CODE

908.0 Gas Fireplaces, Vented.

908.1 Prohibited Installations. Vented gas fireplaces shall not be installed in bathrooms or bedrooms unless the appliance is listed and the bedroom or bathroom has the required volume in accordance with Section 701.2. [NFPA 54:10.7.1]

Exception: Direct-vent gas fireplaces.
 
Don't know about the CA codes, but it is allowed under the I-codes. IFGC 303.3 and IRC G2406.2 both say the same thing:

303.3 Prohibited locations. Appliances shall not be located

in sleeping rooms, bathrooms, toilet rooms, storage closets or

surgical rooms, or in a space that opens only into such rooms

or spaces, except where the installation complies with one of

the following:

1. The appliance is a direct-vent appliance installed in

accordance with the conditions of the listing and the

manufacturer’s instructions.
 