The code does not specify the type of material or construction of the barrier used to identify the level of exit discharge. The key issues to be considered in the selection and approval of the type of barrier to be used are: (1) will the barrier provide a visible and physical means of alerting occupants who are exiting under emergency conditions that they have reached the level of exit discharge and
(2) is the barrier constructed of materials that are permitted by the construction type of the building? In an emergency situation, some occupants are likely to come in contact with the barrier during exiting before realizing that they are at the level of exit discharge. Therefore, the barrier should be constructed in a manner that is substantial enough to withstand the anticipated physical contact, such as pushing or shoving. It would be reasonable, as a minimum, to design the barrier to withstand the structural load requirements of Section 1607.5 for interior walls and partitions. The barrier could be opaque (such as gypsum wallboard and stud framing) or not (such as a wire grid-type material).
The use of signage only or relatively insubstantial barriers, such as ropes or chains strung across the opening, is typically not sufficient to prevent occupants from attempting to continue past the level of exit discharge during an emergency.