Distance to ADA bathroom from office space?
Bill Seegmuller
I was asked by the owner of an office building the following question:
There is an office space on the second floor of his building where the tenant wants to add a bathroom but NOT make it ADA accessible. There is a public ADA accessible bathroom in the hallway outside the office space. Because of this public ADA bathroom, does that preclude the tenant from making his bathroom ADA accessible? I was told the public ADA bathroom has to be within a certain distance from the office.
I have been searching for the answer to this with no luck. I would appreciate any help!
Unless you can comply with one of the (7) exceptions provided in IBC 1109.2, the bathroom shall be constructed with accessible features.
1109.2 Toilet and Bathing Facilities
Each toilet room and bathing room shall be accessible. Where a floor level is not required to be connected by an accessible route, the only toilet rooms or bathing rooms provided within the facility shall not be located on the inaccessible floor. Except as provided for in Sections 1109.2.2 and 1109.2.3, at least one of each type of fixture, element, control or dispenser in each accessible toilet room and bathing room shall be accessible.
1. Toilet rooms or bathing rooms accessed only through a private office, not for common or public use and intended for use by a single occupant, shall be permitted to comply with the specific exceptions in ICC A117.1.
2. This section is not applicable to toilet and bathing rooms that serve dwelling units or sleeping units that are not required to be accessible by Section 1107.
3. Where multiple single-user toilet rooms or bathing rooms are clustered at a single location, at least 50 percent but not less than one room for each use at each cluster shall be accessible.
4. Where no more than one urinal is provided in a toilet room or bathing room, the urinal is not required to be accessible.
5. Toilet rooms or bathing rooms that are part of critical care or intensive care patient sleeping rooms serving Accessible units are not required to be accessible.
6. Toilet rooms or bathing rooms designed for bariatrics patients are not required to comply with the toilet room and bathing room requirement in ICC A117.1. The sleeping units served by bariatrics toilet or bathing rooms shall not count toward the required number of Accessible sleeping units.
7. Where toilet facilities are primarily for children's use, required accessible water closets, toilet compartments and lavatories shall be permitted to comply with children's provision of ICC A117.1.
2015 IPC
403.3.3 Location of toilet facilities in occupancies other
than malls. In occupancies other than covered and open
mall buildings, the required public and employee toilet
facilities shall be located not more than one story above or
below the space required to be provided with toilet facilities,
and the path of travel to such facilities shall not
exceed a distance of 500 feet (152 m).
Exception: The location and maximum distances of
travel to required employee facilities in factory and
industrial occupancies are permitted to exceed that
required by this section, provided that the location and
maximum distance of travel are approved.
Ty ... seems like exception 1 fits the situation.
If you follow exception #1, be forewarned that not much is really exempted. Basically, requires the bathroom to be built in a way that allows it to be easily convertible to an accessible restroom.
I.E. - may not install grab bars, but blocking is still required.
This is what I found as well - The dimensions of the bathroom have to be ADA, but the fixtures do not, and no grab bars are required. This will work for the building owner - they just want a nicely appointed bathroom without the ADA bars and fixtures.
As stated by Ty; you will need to comply with A117.1.
The OP said a second floor office space (aka office suite) wants to add a toilet but not make it acceptable. 1109.2 Exception #1 applies to private bathrooms off of a private office such as executive office with on-suite. If they want to construct a new toilet in the office suite, for use by all employees with in that suite than it has to be accessible.
Grab Bars required in the `17 ANSI A117.1.
Refer to Section 604.5 & Figure 604.5.1.
The 2018 IBC still references the 2009 A117.1 Standard. See IBC Ch. 35 and check the reference.