• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Do all the doors in a Type B Unit need to be a min. of 32" clear?

Ryan Schultz

Registered User
Joined
Apr 2, 2012
Messages
269
Location
Madison, WI
revu_0ta3xpasws.png
 
Nice visual posted. I found this online, please verify.

Type=B units
Doors and Doorways The provisions for doors and doorways are applicable only to doors that are part of the accessible route. Doors that are not part of the accessible route need not comply with ICC/ANSI A117.1 Section 404.
• The primary entrance door to the unit, and all other doorways intended for user passage, shall comply with ICC/ANSI A117.1 Section 404.
• Doorways shall have a clear opening width of 32 inches measured between the face of the door and stop, with the door open 90 degrees. • Openings, doors, and doorways more than 24 inches in depth shall provide a clear opening of 36 inches minimum.
• There shall be no projections into the clear opening width lower than 34 inches above the floor.
• Projections into the clear opening width between 34 and 80 inches above the floor shall not exceed 4 inches.
 