• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Dock stair handrail Q.

SCBO1

Platinum Member
Joined
Oct 28, 2009
Messages
4,367
Location
MID WEST
Dock on a government building not over 30" off grade. A precast set of stairs was set adjacent to the dock and a handrail at 36" was installed on the outside edge with no guard protection. Does this meet code?

Is a dock considered to be a platform? Can't fine much info on a loading dock, a code section would help!

pc1
 
Thanks gb,

1013.1, the railing that is there is not required by code therefore not needing any additional guards. Exception 1 is the only place the word DOCK appears.

pc1
 
Less than 30", a guard is not required, but a code compliant handrail is required for the stair.
 