What type of hose would be required for the flexible connection between the bulkhead and floatiing dock for a Class 3 dock standpipe connection?
I usually see 300 PSI rated fuel hose used. Now I have a contractor that wants to use 150 PSI rated hose who says, of course, he uses it all the time and it will hold a 200 PSI hydro. I can't find anything in NFPA that gives a minimum hose rating for that type of application. I did check some docks around here and some that were legible showed 150 PSI rated and some were 300 PSI rated. I called some neighboring cities and they said their guidelines specify 250 PSI rated hose but they don't know why........:surr
Anyone know a code or NFPA, etc. requirement????
Thanks in advance
I usually see 300 PSI rated fuel hose used. Now I have a contractor that wants to use 150 PSI rated hose who says, of course, he uses it all the time and it will hold a 200 PSI hydro. I can't find anything in NFPA that gives a minimum hose rating for that type of application. I did check some docks around here and some that were legible showed 150 PSI rated and some were 300 PSI rated. I called some neighboring cities and they said their guidelines specify 250 PSI rated hose but they don't know why........:surr