Existing restaurant A-2, with under 100 OL adds a seasonal covered patio seating area adding 32 seats at grade open three sides outside it's door. Now OL is 132, its over 100 requiring a sprinkler system. The 32 occupants could exit through a gate or hop the fence to freedom. Should the 32 seats be added to the occupant load or is there any exemption that I've over looked?
Change in code:
IBC2003 903.2.1.2 Group A-2 (if over 300 occupants require sprinkler)
IBC2006 903.2.1.2 Group A-2 (if over 100 occupants require sprinkler)
Change in code:
IBC2003 903.2.1.2 Group A-2 (if over 300 occupants require sprinkler)
IBC2006 903.2.1.2 Group A-2 (if over 100 occupants require sprinkler)