I will not say where I got this!!!!!!!!!!! I know it is not the code.
1004.8 Outdoor areas. Yards, patios, courts and similar outdoor
areas accessible to and usable by the building occupants
shall be provided with means of egress as required by this chapter.
The occupant load of such outdoor areas shall be assigned
by the building official in accordance with the anticipated use.
Where outdoor areas are to be used by persons in addition to the
occupants of the building, and the path of egress travel from the
outdoor areas passes through the building, means of egress
requirements for the building shall be based on the sum of the
occupant loads of the building plus the outdoor areas.
Exceptions:
1. Outdoor areas used exclusively for service of the
building need only have one means of egress.
2. Both outdoor areas associated with Group R-3 and
individual dwelling units of Group R-2.
This section addresses the means of egress of outdoor
areas such as yards, patios and courts. The primary
primary
concern is for those outdoor areas used for functions
that may include occupants other than the building
occupants, or solely by the building occupants
where egress from the outdoor area is back through
the building to reach the exit discharge. An example is
an interior court of an office building where assembly
functions are held during normal business hours for
persons other than the building occupants. When
court occupants must egress from the interior court
back through the building, the building’s egress system
is to be designed for the building occupants, plus
the assembly occupants from the interior court. Another
example would be an outdoor dining area that
exited back through the restaurant.
The occupant load is to be assigned by the building
official based on use. It is suggested that the design
occupant load be determined in accordance with Section
1004.1.1.
The exceptions describe conditions where the combination
of occupant loads is not a concern.
1004.1.1 Areas without fixed seating.
The design occupant load is also utilized for other
code requirements, such as determining the required
plumbing fixture count (see commentary, Chapter 29)
and other building requirements, including automatic
sprinkler systems and fire alarm and detection systems
But then comes this:
Some occupancies may not typically contain
an occupant load totally consistent with the occupant
load density factors of Table 1004.1.2. The exception
is intended to address the limited circumstances
where the actual occupant load is less than the calculated
occupant load. Previously, designing for a reduced
occupant load was permitted only through the
variance process. With this exception, the building official
can make a determination if a design that would
use the actual occupant load was permissible. The
building official may want to create specific conditions
for approval. For example, the building official could
permit the actual occupant load to be utilized to determine
the plumbing fixture count, but not the means of
egress or sprinkler design; the determination could be
that the reduced occupant load may be utilized in a
specific area, such as in the storage warehouse, but
not in the factory or office areas.