nealderidder

Sawhorse
Joined
Dec 7, 2010
Messages
431
Location
Sacramento, CA
I'm doing some code spelunking because I have a door at a landing on an exterior stairway that doesn't quite meet the 5' clear door maneuvering clearance. It's close but the handrail protrudes into the clear floor space a few inches. I'm reviewing shop drawings and looking for adjustments to provide that 5' clearance.

And then I run across CBC 11B-207.1 Exception #4: Doors that provide access only to interior or exterior stairways shall not be required to comply with 11B-404.

How have I missed this? I don't need to provide door maneuvering clearances at stairway doors?
 
Added in 2022. Seems a little crazy right............ but that is how I read it too. Often times there are issues with existing door clearances from the stair side if you would reenter the space but I typically do not tag those as I view the door as an exit only condition. I do perhaps go above and beyond the 2022 code and tag clearance issues when entering the stair.
 
Recent discussion:
Thanks SIFU, interesting reading. Looks like the exception I listed is a CA thing. So the conclusions in that thread don't apply. The CBC flat out states that stairway doors don't need maneuvering clearance (the bolded excerpt above in my first post).
 
Neal, J Pohling and others:
That Exception was not _added_ in the 2022 CBC. It has always been there, but few noticed it because it was under Section 11B-206.4.1 on "Entrances and exterior ground floor exits." For example, here is a screenshot from the original 2019 CBC:

1733188117662.png

When the DSA proposed relocating the Exception to Section 11B-207, they stated in their Initial Statement of Reasons (ISOR) that they were merely moving the provisions, not changing their meaning or intent:1733187989929.png

Despite whiny blowback from a particularly overzealous but grievously mistaken CASP (whom my firm had the misfortune of working with on a UC project), the DSA stuck to its guns and the provision was adopted. So if you have any public accommodation project under a code earlier than the 2022 CBC, the Exception would still apply to exit only stair doors.
 