Why was this failed?
Plastic bushings for securing NM were properly installed.Fortner said:I don't see any box connectors for the NM. Was the metallic box bonded? I believe you have to protect that doorbell transformer from damage also. Why is a GFI receptacle in the attic?
Article 450 does not apply to Class 2 and 3 transformers.Fortner said:450.21 (A)
There is no mixing of voltages in the same enclosure in this example.georgia plans exam said:Would it have to do with the mixing of voltage ratings in the same enclosure???GPE
BINGO!!raider1 said:The transformer would be marked "Not for installation in an attic" so 110.3(B) would be the applicable code section to fail this installation.Chris
The Class 2 conductors are not located in the same box with the power conductors.vegas paul said:725.136 (A)