In a S-1 warehouse with an occupant load of less than 30, does it need a drinking facility?
California, using CPC / Uniform Plumbing Code. Occupant load is 26.
CPC 415.2 states that you don't need a drinking fountain in a building if the occupant load of the building is less than 30. However, Table 422.1 states that a "drinking fountain / facility" is required regardless of the occupant load (1 required if the occupant load is between 1-250).
Does CPC 415.2 override the requirements of Table 422.1? Is a drinking facility required in this case or can I exclude that?
California, using CPC / Uniform Plumbing Code. Occupant load is 26.
CPC 415.2 states that you don't need a drinking fountain in a building if the occupant load of the building is less than 30. However, Table 422.1 states that a "drinking fountain / facility" is required regardless of the occupant load (1 required if the occupant load is between 1-250).
Does CPC 415.2 override the requirements of Table 422.1? Is a drinking facility required in this case or can I exclude that?