Drip pans for hydronic piping in electrical room?

HVACQuestions

REGISTERED
Joined
Sep 23, 2019
Messages
23
Location
02210
I was looking in IMC, are there any code requirements for drip pans under hydronic piping in an electrical room? The only time I've seen it was as good practice, not a specific code requirement.
 
2014 NEC 110.26
(1) indoor
(a)Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 6' above the equipment or to the structural ceiling, which ever is lower, shall be dedicated to the electrical installation. No pipes, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 6' zone.
(b) Foreign Systems. The area above the dedicated space by (a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
 
2014 NEC 110.26
(1) indoor
(a)Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 6' above the equipment or to the structural ceiling, which ever is lower, shall be dedicated to the electrical installation. No pipes, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 6' zone.
(b) Foreign Systems. The area above the dedicated space by (a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
Thank you!
 