I have been under the impression the typical fire separation wall in residential construction, single family was 5/8 "firecode" on the garage side.
As a matter of fact, to comply to a resale inspection, I had to rock this certain "illegal" laundry room in a garage, overlaying the existing 1/2" with 5/8", to the sheathing. Requirement by the city inspectigator. Typical in my understanding.
So one street over I do the same thing today, where I had reframed the illegal laundry in the garage, back to the house to comply with mandated off street parking requirement. Inspectigator says I don't have to use 5/8 any longer, been that way since the 2010 residential code that I guess trumps UBC.
So, as can sometimes happen, apparently the right hand knows not the activities of the left.
Can anyone clarify, maybe with the code section to point to?
Kind of a moot point for me as I will probably do it the old way just to spite myself, but just interested in the truth of this conspiracy.
Thanks,
Brent.
R302.6 Dwelling/garage fire separation. The garage shall be separated as required by Table R302.6. Openings in garage walls shall comply with Section R302.5. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.
TABLE R302.6 DWELLING/GARAGE SEPARATION
SEPARATION
MATERIAL
From the residence and attic Not less than 1⁄2-inch gypsum board or equivalent applied to the garage side
From all habitable rooms above the garage Not less than 5⁄8-inch Type X gypsum board or equivalent
Structure(s) supporting floor/ceiling assemblies used for separation required by this section Not less than 1⁄2-inch gypsum board or equivalent
Garages located less than 3 feet from a dwelling unit on the same lot Not less than 1⁄2-inch gypsum board or equivalent applied to the interior side of exterior walls that are within this area
The table does not copy correctly;;;;
http://publicecodes.cyberregs.com/icod/irc/2009/icod_irc_2009_3_par058.htm
cda said:
R302.6 Dwelling/garage fire separation. The garage shall be separated as required by Table R302.6. Openings in garage walls shall comply with Section R302.5. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall. TABLE R302.6 DWELLING/GARAGE SEPARATION
SEPARATION
MATERIAL
Residential garage fires comprise about 2 percent of all residential building fires.
http://www.nfpa.org/~/media/Files/Research/NFPA%20reports/Occupancies/oshomes.pdf
It was determined. by the code writers, based on that, we do not need to protect the house from the lower risk, garage
But some jurisdictions, still require 5/8” gyp bd.
Brent, 1/2" unless the AHJ modifies the table to 5/8 FC.
Could't you get approved with two layers of 1/2" with longer nails or screws? You could stager the joints, you would be a hero!
What about those receptacle box extensions?
Pc1
Pcinspector1 said:
Brent, 1/2" unless the AHJ modifies the table to 5/8 FC. Could't you get approved with two layers of 1/2" with longer nails or screws? You could stager the joints, you would be a hero!
Pc1
I honestly don't know if 2 layers rate the same as 1 of 5/8. It looks like I'm a retard on fire assemblies in general so I'll brush up on that shortly.
I haven't run into a short box yet, probably just gut a plastic one or put a 1 inch mudring on a metal box if it came to that.
Oh...I'm a hero in general terms. Thought you should know that.
Brent.
two 1/2 inch laers does not equate to 1 layer of 5/8 inch....
TABLE 722.6.2(1) TIME ASSIGNED TO WALLBOARD MEMBRANESa, b, c, d
DESCRIPTION OF FINISH TIMEe (minutes)
3/8-inch wood structural panel bonded with
exterior glue 5
15/32-inch wood structural panel bonded with
exterior glue 10
19/3 -inch wood structural panel bonded with
exterior glue 15
3/8-inch gypsum wallboard 10
1/2 -inch gypsum wallboard 15
5/8 -inch gypsum wallboard 30
1/2-inch Type X gypsum wallboard 25
5/8-inch Type X gypsum wallboard 40
Double 3/8-inch gypsum wallboard 25
1/2-inch + 3/8-inch gypsum wallboard 35
Double 1/2-inch gypsum wallboard 40
Builder Bob said:
two 1/2 inch laers does not equate to 1 layer of 5/8 inch....TABLE 722.6.2(1) TIME ASSIGNED TO WALLBOARD MEMBRANESa, b, c, d
exterior glue 5
exterior glue 10
exterior glue 15
1/2-inch Type X gypsum wallboard 25 x2 =50
50 greater than 40, not equal, Better....
BB & Mark, good info!
Finding 1/2"FC (type-x) drywall is probably going to be a specialty product from a drywall house and regular 1/2" cost you over $10.00 bucks @ the box store = $20.00.
Cheaper to get the 5/8"FC to get the results you need in minutes. Not to mention it might mess with your window and door frame widths costing you more $$.
"That's what speed do!" Jarod Dyson, KC Royals
pc1
5/8" Type X is the prescriptive provision in most IRC based codes. Those Codes generally still allow for a approved deign for a 3/4 hour rated assembly, and UL has many 1 hour walls with 1/2" GWB on both sides.
Methinks your inspectigator needs to read his Code more thoroughly...
"Sometimes it makes no sense to fight city hall, and 5/8" is standard issue."
Bingo, install 5'8", then no questions are asked.
FWIW, we amended the 1/2" to 5/8" when we moved over from the 97 UBC to the 2003 IRC.................
What's funny is the walls in question are the easyist to do in whatever rock.
If you want to do me a favor make the ceiling 1/2".
Makes me wonder what the point of downgrading is was. Considering the general freak out associated with fire risk.
Brent.
MASSDRIVER said:
Makes me wonder what the point of downgrading is was. Considering the general freak out associated with fire risk. Brent.
mark handler said:
Residential garage fires comprise about 2 percent of all residential building fires.http://www.nfpa.org/~/media/Files/Research/NFPA%20reports/Occupancies/oshomes.pdf
But how do the statistics factor the percentage of houses without garages? Fire can't start in a place you don't have!?
Just one of the dangers of allowing statisticians input on Code and Standard development. :wink:
Mass, Covering the I-beam and post with drywall?
Just keepin yo in line! Inspectigator will be back!
pc1
mjesse said:
But how do the statistics factor the percentage of houses without garages? Fire can't start in a place you don't have!?Just one of the dangers of allowing statisticians input on Code and Standard development. :wink:
Because if you did you would instantly have no need for Gfci, or arc fault, or half the stuff in the Strong tie catalog.
Brent.
We see this requirement missed a lot since it is hidden in the wall covering portion of the code
IRC Table R702.3.5 foot note d
e. Type X gypsum board for garage ceilings beneath habitable rooms shall be installed perpendicular to the ceiling framing and shall be fastened at maximum 6 inches o.c. by minimum 17/8 inches 6d coated nails or equivalent drywall screws.