My imediateimpression is: Seems like the fire wall height ( I know it isn't directly referenced) of what 30" or 36" above 1st floor roof should or could be FR plywood as a minimum to insure the integrity of the Rated Assembly.If it is a two family dwelling, then no, it does not.
The IRC requires separation of the dwelling units. As there is not a portion of the dwelling unit adjacent to the Unit A upper floor, separation is not required.
R302.3 Two-Family Dwellings
Dwelling units in two-family dwellings shall be separated from each other by wall and floor assemblies having not less than a 1-hour fire-resistance rating where tested in accordance with ASTM E119, UL 263 or Section 703.3 of the International Building Code. Fire-resistance-rated floor/ceiling and wall assemblies shall extend to and be tight against the exterior wall, and wall assemblies shall extend from the foundation to the underside of the roof sheathing.
Exceptions:That said, some AHJ may tell you that you need to treat the wall as an exterior wall and require 1-hr construction given the lack of fire separation distance. This stance may be tough to counter, but you can attempt to sway them with the via the forthcoming 2021 code language. See this Building Journal Article by ICC and/or the ICC Significant Change Summary.
- A fire-resistance rating of 1/2 hour shall be permitted in buildings equipped throughout with an automatic sprinkler system installed in accordance with NFPA 13.
- Wall assemblies need not extend through attic spaces where the ceiling is protected by not less than 5/8-inch (15.9 mm) Type X gypsum board, an attic draft stop constructed as specified in Section R302.12.1 is provided above and along the wall assembly separating the dwellings and the structural framing supporting the ceiling is protected by not less than 1/2-inch (12.7 mm) gypsum board or equivalent.
And maybe the horizontal 4ft on the 1st floor roof as well?My imediateimpression is: Seems like the fire wall height ( I know it isn't directly referenced) of what 30" or 36" above 1st floor roof should or could be FR plywood as a minimum to insure the integrity of the Rated Assembly.