I am working on a large complex of garden style apartment buildings. An egress balcony connects buildings considered part of the same building per IBC as they are within the allowable height and area. We would like to use the same egress balcony to connect buildings that are considered separate buildings and separated by an imaginary property line. This would effectively bridge the two buildings. I am a uncertain what rating, if any applies to this section of the egress balcony, or if this is even permitted. Part of the purpose of this egress balcony is to eliminate a dead end corridor, so it would be creating a situation where egress could pass from one building to the other. 1021.4 talks about fire separation distance, but measured at right angles from the exterior edge, in this situation there is an imaginary property line perpendicular to the egress balcony, but adjacencies would run parallel to the edge, if that makes sense. The exterior walls of the buildings require a one hour rating. It is type VB construction and the fire separation distance for each building from the imaginary property line is 5'