Where in Ontario building code is this egress clearance of exit stairs prescribed?
Should the code is 3.4.3.4.(1).?...
Code reference for limiting the obstruction to be no more than the exit width is 3.4.3.3(1).
FYI: I'm assuming a part 3 building given the standpipe.
NBC 2015 3.4.3.4 is headroom clearance. 3.4.3.3 is "exit width reduction."Should the code is 3.4.3.4.(1).?
Correct, the standpipe required by part 3.
Yep. Lesson for us all is to note which Code we're using - BCBC, ABC, OBBC, NBC. (Or, alors, le QBC.)You are both talking about the same code provision. Number is slightly different between versions.
Understood.Your exit width is set 3.4.3.2.(OBC) based on occupancy load and a few other factors. The stairs are by definition an exit. From the top right down to the discharge door. The width would need to be maintained throughout the stairs. Exceptions that allow things to protrude into the exit are contained in 3.4.3.4. (OBC).
If there is not an exception allowing something to reduce the exit width, no reduction would be permitted.
There is nothing that would indicate if it must be measured as a semi-circle as shown, or rectangular.Understood.
My question basically comes down to:
can the exit width be measured as the radius centered at the nose of the handrail shown in the picture given in my post? Which clause in OBC allows this measurement?
That is what I typically see on drawings. It allows for the standpipe to remain in the corner and not foul the egress path.Understood.