2012 IBC. I am working with a developer in partnership with the City to develop a 4 story mixed use building with residential (R-2) above the egress at grade level. The City operates a 5 story parking garage (S-2) on the adjacent lot. The intent is to use the existing elevator in the parking garage as the accessible means of egress for the upper floors of the R-2. Only one new egress stair is planned connecting all levels to the exterior. The second means of egress at each floor is to be a horizontal exit through the required fire wall assembly into the parking garage adjacent to the garage egress stair. Questions:
1. Can we use a horizontal exit between buildings owned by two separate entities on different lots?
2. If the horizontal exit is allowed is this a violation of 1014.2 since the egress would be from a lower hazard (R-2) into a higher hazard (S-2).
3. To use the elevator of the S-2 parking garage it appears that we would have to wrap the elevator with a 2hr fire wall with self-closing fire doors to protect the elevator shaft openings. Are there any other protectives required?