Hello Folks.
My team and I are in the preliminary design phase for a fire station in the suburb of Seattle area. The building has two stories which requires two interior exit stairways. The code is IBC 2018. Please see the Level 1 plan from the attached link. The most of the occupancy in the shown administrative area is Business while Sleeping Rooms (SR) are R-2. The assembly type is 5B.
Both stairways have 1 hour-rated enclosure at the Level 2 while its open to the corridor on the level 1.
I understand that IBC 1016.2 permits the egress from 50% of interior exit stair pass through elevator lobby. However, our lobby is not the "elevator lobby" mentioned in IBC 1016.2. In my understanding, the "elevator lobby" in 1016.2 is 1 hour-rated enclosed elevator lobby.
The common knowledge tells me that the egress from one of those stair (stair #1) is allowed to intervene the entrance lobby while the other (stair #2) NEED TO DIRECTLY EGRESS TO OUTSIDE. However, I'm having difficulty to find the solid proof for this in the Chapter 10. I am wondering that this may be interpreting the 1016.2 mistakenly.
If only the egress from stair #1 is allowed to intervene other space, the stair #2 need be flipped so that it can egress directly to outside. However, we don't want to do this for fire fire fighters who are working upstairs to respond quickly, and move down to the Apparatus Bay (Pink area at the bottom of plan) in case of emergency.
One of my coworker suggested that the lobby may not be recognized as intervening space. I assume this is because the stair is not enclosed on the Level 1. If this is true, I can maintain the stair #2 as it is currently. However, I cannot find a proof for this in the Chapter 10 neither. Can anyone advise please?
Thank you !
Plan
My team and I are in the preliminary design phase for a fire station in the suburb of Seattle area. The building has two stories which requires two interior exit stairways. The code is IBC 2018. Please see the Level 1 plan from the attached link. The most of the occupancy in the shown administrative area is Business while Sleeping Rooms (SR) are R-2. The assembly type is 5B.
Both stairways have 1 hour-rated enclosure at the Level 2 while its open to the corridor on the level 1.
I understand that IBC 1016.2 permits the egress from 50% of interior exit stair pass through elevator lobby. However, our lobby is not the "elevator lobby" mentioned in IBC 1016.2. In my understanding, the "elevator lobby" in 1016.2 is 1 hour-rated enclosed elevator lobby.
The common knowledge tells me that the egress from one of those stair (stair #1) is allowed to intervene the entrance lobby while the other (stair #2) NEED TO DIRECTLY EGRESS TO OUTSIDE. However, I'm having difficulty to find the solid proof for this in the Chapter 10. I am wondering that this may be interpreting the 1016.2 mistakenly.
If only the egress from stair #1 is allowed to intervene other space, the stair #2 need be flipped so that it can egress directly to outside. However, we don't want to do this for fire fire fighters who are working upstairs to respond quickly, and move down to the Apparatus Bay (Pink area at the bottom of plan) in case of emergency.
One of my coworker suggested that the lobby may not be recognized as intervening space. I assume this is because the stair is not enclosed on the Level 1. If this is true, I can maintain the stair #2 as it is currently. However, I cannot find a proof for this in the Chapter 10 neither. Can anyone advise please?
Thank you !