• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Electric convection oven hood

If it's above a "commercial cooking appliance", and the exceptions of 507.1 do not apply, then 507.2 does. Hood required.
 
2009 IMC section 507.2.2--this is new to the 2009 edition, so it does not apply to erlier editions--allows electric only appliances that would normally be under a type II hood to have no hood as long as the extra heat and moisture loads are accounted for in the HVAC system. In addition, for each appliance not under a hood, 100 sq. ft. is added to the floor area required to be ventilated in the kitchen per section 403.3. Gas appliances still require a hood under any circumstances to remove products of combustion.
 
I always look at the spec's for the oven. some require a hood and some don't as long as it is vented to the specs. I always look to make sure the HVAC system is able to handle the extra heat and moister.

Justin
 