Electric Room Doors

LGreene

REGISTERED
Joined
Oct 20, 2009
Messages
1,166
Location
San Miguel de Allende, Mexico
Can someone tell me when an electric room would require two doors? A facility manager has an electric room with a door to the interior and a door to the exterior. He wants to get rid of the door to the interior. This is outside my area of expertise, but I'd at least like to tell him where to look it up. We're currently using the 2003 IBC and the 2008 NEC.
 
I will post the text from 110.26©

© Entrance to and Egress from Working Space.(1) Minimum Required. At least one entrance of sufficient area shall be provided to give access to and egress from working space about electrical equipment.

(2) Large Equipment. For equipment rated 1200 amperes or more and over 1.8 m (6 ft) wide that contains overcurrent devices, switching devices, or control devices, there shall be one entrance to and egress from the required working space not less than 610 mm (24 in.) wide and 2.0 m (6½ ft) high at each end of the working space.

A single entrance to and egress from the required working space shall be permitted where either of the conditions in 110.26©(2)(a) or ©(2)(b) is met.

(a) Unobstructed Egress.Where the location permits a continuous and unobstructed way of egress travel, a single entrance to the working space shall be permitted.

(b) Extra Working Space. Where the depth of the working space is twice that required by 110.26(A)(1), a single entrance shall be permitted. It shall be located such that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition.
Chris
 
Thanks GPE and Chris...I found the info in the free online version of the NEC, but it was nice to have the text to cut and paste since you can't do that with the free version.
 