• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Electrical Inspector Trivia

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
10,971
Location
Somewhere Too Hot & Humid
What is the minimum branch circuit wire size and overcurrent protection device for the installation of this pool heater?
This is fed by a 120/208v single phase panelboard.
IMG_7840.jpg
 
#8 conductors (75 or 90 C) are good for 43 amps.

I'd use the maximum breaker size as the minimum to avoid tripping when the compressor starts.
 
41.81x 1.25 = 52.26 amps. 6awg conductors with a 60 amp breaker assuming the heater will be on for 3 or more hours making it a continuous load.
 