no requirement for drywall on the house side here, could be thin wood paneling.we do not allow unfused service entrance conductors inside the building, we want a service disconnect on the outside of the building, and properly installed romex is protected .Pcinspector1 said:I would'nt think it would create a breech as long as the other side has a min. 1/2" drywall behind the panel, would'nt that be the same as a GFCI outlet or a light switch in that same wall? Also consider whats being installed behind that panel box, protecting service entrance wires and romex should be considered.
pc1
Since it is not a rated wall; does fireblocking material such as unfaced fiberglass insulation packed tightly around the obstruction qualify as "approved material to resist the free passage of flame and products of combustion" (R602.8.1.1) or is none required since the electrical covers and face plates block the opening?R309.1.2 Other penetrations.
Penetrations through the separation required in Section R309.2 shall be protected by filling the opening around the penetrating item with approved material to resist the free passage of flame and products of combustion.