Electrical Room Fire Sprinklers

TFM

Member
Joined
Feb 22, 2012
Messages
6
I have a few electrical rooms with transformers in them with fire sprinkler heads right above them, what is the distance from the fire sprinkler heads to the transformers? Also is there a distance requirement from the branchlines to the transformer? Existing building...Thanks..
 
there use to are still is something about shielding the transformers, above a certain size, cannot find it.

maybe it is in a version of nfpa 70

as far as spacing would be per the listing of the head.
 
got burried from the 2007 :::

8.15.10 Electrical Equipment.

8.15.10.1 Unless the requirements of 8.15.10.3 are met, sprinkler protection shall be required in electrical equipment rooms.

8.15.10.2 Hoods or shields installed to protect important electrical equipment from sprinkler discharge shall be noncombustible.

8.15.10.3 Sprinklers shall not be required in electrical equipment rooms where all of the following conditions are met:

(1)

The room is dedicated to electrical equipment only.

(2)

Only dry-type electrical equipment is used.

(3)

Equipment is installed in a 2-hour fire-rated enclosure including protection for penetrations.

(4)

No combustible storage is permitted to be stored in the room.

http://www.usfa.fema.gov/downloads/pdf/coffee-break/cb_2008_36.pdf
 