Glennman CBO
Silver Member
- Joined
- Oct 20, 2009
- Messages
- 441
2006 IBC 1104.4 and 1108.2.8
The exception under 1108.2.8 appears to allow elevated dining areas under 3000 sq ft to be unaccessible (per 1104.4 exception 1) as long as the same level of service is provided in the accessible areas, with the exception of mezzanines that are over 25% of the total area of the accessible levels. Am I reading this right?
"In buildings or facilities not required to provide an accessible route between levels...". I would take this as referring to 3000 sq ft or less levels that are allowed to not have an accessible route to them per 1104.4.
It appears that exception #1 to 1108.2.8 removes only the mezzenine portion of the exception under 1104.4, and therefore still allows the other levels of inaccessibility under 3000 sq ft. as long as these are not mezzaanines (?).
Thoughts?
The exception under 1108.2.8 appears to allow elevated dining areas under 3000 sq ft to be unaccessible (per 1104.4 exception 1) as long as the same level of service is provided in the accessible areas, with the exception of mezzanines that are over 25% of the total area of the accessible levels. Am I reading this right?
"In buildings or facilities not required to provide an accessible route between levels...". I would take this as referring to 3000 sq ft or less levels that are allowed to not have an accessible route to them per 1104.4.
It appears that exception #1 to 1108.2.8 removes only the mezzenine portion of the exception under 1104.4, and therefore still allows the other levels of inaccessibility under 3000 sq ft. as long as these are not mezzaanines (?).
Thoughts?