Elevated Platform @Terrace Guardrail Requirements

m310

REGISTERED
Joined
Jul 2, 2024
Messages
2
Location
Baltimore
1719953358813.png
Trying to determine the required height of guardrail (dimension A) at an elevated terrace, but having a surprisingly hard time to find an answer across OSHA and the IBC. To describe the image above, from left to right: 2'-9" is a projection into the void. In pink, a vertical guardrail (A) is drawn, with a perimeter maintenance path of the terrace behind it (dimension C). A 1'-6" tall and 1'-0" wide curb separates this perimeter maintenance path from a planter area on terrace (not occupiable), which has a mirrored curb separating the planter and the "deck" area of the terrace, which is at the same height as the maintenance path.

I'm looking for any advice on where to find answers to the required dimensions of A; B and C.
 
1015.1 General. Guards shall comply with the provisions of
Sections 1015.2 through 1015.7. Operable windows with sills
located more than 72 inches (1829 mm) above finished grade
or other surface below shall comply with Section 1015.8.
1015.2 Where required. Guards shall be located along
open-sided walking surfaces, including mezzanines, equipment
platforms, aisles, stairs, ramps and landings that are
located more than 30 inches (762 mm) measured vertically to
the floor or grade below at any point within 36 inches (914
mm) horizontally to the edge of the open side. Guards shall
be adequate in strength and attachment in accordance with
Section 1607.8.
Exception: Guards are not required for the following
locations:
1. On the loading side of loading docks or piers.
2. On the audience side of stages and raised platforms,
including stairs leading up to the stage and raised
platforms.
3. On raised stage and platform floor areas, such as
runways, ramps and side stages used for entertainment
or presentations.
4. At vertical openings in the performance area of
stages and platforms.
5. At elevated walking surfaces appurtenant to stages
and platforms for access to and utilization of special
lighting or equipment.
6. Along vehicle service pits not accessible to the public.
7. In assembly seating areas at cross aisles in accordance
with Section 1029.17.2.
1015.2.1 Glazing. Where glass is used to provide a guard
or as a portion of the guard system, the guard shall comply
with Section 2407. Where the glazing provided does
not meet the strength and attachment requirements of Section
1607.8, complying guards shall be located along
glazed sides of open-sided walking surfaces.
1015.3 Height. Required guards shall be not less than 42
inches (1067 mm) high, measured vertically as follows:
1. From the adjacent walking surfaces.
2. On stairways and stepped aisles, from the line connecting
the leading edges of the tread nosings.
3. On ramps and ramped aisles, from the ramp surface at
the guard.
Exceptions:
1. For occupancies in Group R-3 not more than three
stories above grade in height and within individual
dwelling units in occupancies in Group R-2 not
more than three stories above grade in height with
separate means of egress, required guards shall be
not less than 36 inches (914 mm) in height measured
vertically above the adjacent walking surfaces.
2. For occupancies in Group R-3, and within individual
dwelling units in occupancies in Group R-2, guards
on the open sides of stairs shall have a height not
less than 34 inches (864 mm) measured vertically
from a line connecting the leading edges of the
treads.
3. For occupancies in Group R-3, and within individual
dwelling units in occupancies in Group R-2, where
the top of the guard serves as a handrail on the open
sides of stairs, the top of the guard shall be not less
than 34 inches (864 mm) and not more than 38
inches (965 mm) measured vertically from a line
connecting the leading edges of the treads.
4. The guard height in assembly seating areas shall
comply with Section 1029.17 as applicable.
5. Along alternating tread devices and ship’s ladders,
guards where the top rail serves as a handrail shall
have height not less than 30 inches (762 mm) and not
more than 34 inches (864 mm), measured vertically
from the leading edge of the device tread nosing.
6. In Group F occupancies where exit access stairways
serve fewer than three stories and such stairways are
not open to the public, and where the top of the guard
also serves as a handrail, the top of the guard shall be
not less than 34 inches (864 mm) and not more than
38 inches (965 mm) measured vertically from a line
connecting the leading edges of the treads.
1015.4 Opening limitations. Required guards shall not have
openings that allow passage of a sphere 4 inches (102 mm) in
diameter from the walking surface to the required guard
height.
Exceptions:
1. From a height of 36 inches (914 mm) to 42 inches
(1067 mm), guards shall not have openings that
allow passage of a sphere 43/8 inches (111 mm) in
diameter.
2. The triangular openings at the open sides of a stair,
formed by the riser, tread and bottom rail shall not
allow passage of a sphere 6 inches (152 mm) in
diameter.
3. At elevated walking surfaces for access to and use of
electrical, mechanical or plumbing systems or
equipment, guards shall not have openings that
allow passage of a sphere 21 inches (533 mm) in
diameter.
4. In areas that are not open to the public within occupancies
in Group I-3, F, H or S, and for alternating
tread devices and ship’s ladders, guards shall not
have openings that allow passage of a sphere 21
inches (533 mm) in diameter.
5. In assembly seating areas, guards required at the end
of aisles in accordance with Section 1029.17.4 shall
not have openings that allow passage of a sphere 4
inches (102 mm) in diameter up to a height of 26
inches (660 mm). From a height of 26 inches (660
mm) to 42 inches (1067 mm) above the adjacent
walking surfaces, guards shall not have openings
that allow passage of a sphere 8 inches (203 mm) in
diameter.
6. Within individual dwelling units and sleeping units
in Group R-2 and R-3 occupancies, guards on the
open sides of stairs shall not have openings that
allow passage of a sphere 43/8 (111 mm) inches in
diameter.
 
into the void
So this void is what, like the edge of a roof or something? What’s the vertical distance from the edge of the void to the closest walking surface below?

with a perimeter maintenance path of the terrace behind it (dimension C)
Assuming the vertical distance from the walking path to the bottom of the void is more than 30”, and because the distance from the edge of the path to the edge of the void is greater than 36” (both per IBC 1015.2,) you will need a guard that is 42” high per IBC 1015.3. This 42” is your A dimension, B is 42” - 18” = 24”.

As for your C dimension, does this area need to be accessible?

Are there people walking to the right of the curb?

to find an answer across OSHA
Sorry, I can’t comment on the OSHA requirements, maybe someone else can.
 
correct, void is edge of roof. approximate height is 40feet above sidewalk. I'm mainly wondering if I need to take into account the elevated platform (which is really the planter that is not occupiable, separated by that 1foot wide curb) and thus have the dimension B account for that somehow? Say the C dimension is only 1'-6" as a maintenance path, would it be acceptable to have that elevated planter (not occupiable) so close to a guardail, as tall as you describe?
 
void is edge of roof. approximate height is 40feet above sidewalk.
Oh, yeah, that’s more than a 30” change in elevation!

I'm mainly wondering if I need to take into account the elevated platform (which is really the planter that is not occupiable, separated by that 1foot wide curb) and thus have the dimension B account for that somehow?
The guard protects the adjacent walking surface, as long as the raised area on the right with the 12” wide curb truly is not an occupied area then the code does not require the 42” to be measured from the top of the curb.

The designer needs to consider if there is a chance some kid is going to test their jumping skills and jump over the path from the curb and see if they can make it over the guardrail. If it’s a restricted area only for maintenance staff that shouldn’t be an issue.

with a perimeter maintenance path of the terrace behind it (dimension C).
As for the width C on your drawing. The path is an aisle, per IBC 1018.3 and 1018.5 widths of aisles are the same as for corridors. Corridor width is in 1020.2, per Table 1020.2 with an occupant load of less than 50 you can have a 36” wide path (aisle.)
 