klarenbeek
REGISTERED
Commercial building with underground parking, with the boiler room separated from the garage by a single door. The design of the boilers is such that all sources of ignition are at least 18" above the floor. The circulation pumps (12 of them) are all on housekeeping pads, but the motors, etc. are less than 18" above the primary floor. Here's the relevant code section from the 2021 IMC:
304.3 Elevation of ignition source.
Equipment and appliances having an ignition source and located in hazardous locations and public garages, private garages, repair garages, automotive motor fuel-dispensing facilities and parking garages shall be elevated such that the source of ignition is not less than 18 inches (457 mm) above the floor surface on which the equipment or appliance rests. For the purpose of this section, rooms or spaces that are not part of the living space of a dwelling unit and that communicate directly with a private garage through openings shall be considered to be part of the private garage.
Exception: Elevation of the ignition source is not required for appliances that are listed as flammable vapor ignition resistant.
304.3.1 Parking garages.
Connection of a parking garage with any room in which there is a fuel-fired appliance shall be by means of a vestibule providing a two-doorway separation, except that a single door is permitted where the sources of ignition in the appliance are elevated in accordance with Section 304.3.
Exception: This section shall not apply to appliance installations complying with Section 304.6.
The way I'm reading this, since the pumps are not located in the garage but in a room adjacent to the garage, they do not need to be elevated. This is a public garage not private, so the last sentence of 304.3 does not apply. 304.3.1 requiring the two doorway separation only applies to fuel fired appliances but not to equipment, which is what the pumps are. A single door is all that is required since the boilers themselves meet the elevation requirement.
I don't necessarily like it, but that's what I'm seeing. Thoughts?
304.3 Elevation of ignition source.
Equipment and appliances having an ignition source and located in hazardous locations and public garages, private garages, repair garages, automotive motor fuel-dispensing facilities and parking garages shall be elevated such that the source of ignition is not less than 18 inches (457 mm) above the floor surface on which the equipment or appliance rests. For the purpose of this section, rooms or spaces that are not part of the living space of a dwelling unit and that communicate directly with a private garage through openings shall be considered to be part of the private garage.
Exception: Elevation of the ignition source is not required for appliances that are listed as flammable vapor ignition resistant.
304.3.1 Parking garages.
Connection of a parking garage with any room in which there is a fuel-fired appliance shall be by means of a vestibule providing a two-doorway separation, except that a single door is permitted where the sources of ignition in the appliance are elevated in accordance with Section 304.3.
Exception: This section shall not apply to appliance installations complying with Section 304.6.
The way I'm reading this, since the pumps are not located in the garage but in a room adjacent to the garage, they do not need to be elevated. This is a public garage not private, so the last sentence of 304.3 does not apply. 304.3.1 requiring the two doorway separation only applies to fuel fired appliances but not to equipment, which is what the pumps are. A single door is all that is required since the boilers themselves meet the elevation requirement.
I don't necessarily like it, but that's what I'm seeing. Thoughts?