I have a project that I would like your collective thoughts on, because I think it is something that seems to have fallen through the cracks of the current code.
The situation is this, an existing 4-story hotel has an occupied roof. The occupied roof was added about six years ago. There are two exterior stairs that lead from the roof and have more than enough egress capacity. The problem is this, the elevator does not extend to the roof, so the owner obtained a permit to extend the elevator shaft to the roof (i.e. a fifth floor).
The elevator work is installed, but now the inspector is requiring that standby power be provided for the elevator per Section 1007.2.1 (2012 IBC), which requires that an elevator be one of the accessible means of egress (because there is now a "floor" that is more than 4 stories above the level of exit discharge), which, in turn, is required to have standby power per Section 1007.4. The cost of adding standby power far exceeds the cost of extending the elevator to the roof, which the owner did not anticipate and was not mentioned during the plan review. If the owner had known this during plan review, he may not have proceeded with the work.
Now I've been hired to draft a code modification that would justify why standby power is not necessary. The owner try to argue that they were altering an existing elevator and that the elevator would not be required to comply with all of the requirements for new construction, just the portion that was altered. The city countered that the shaft extension is actually an "addition," thus requiring full compliance with the IBC. The elevator shaft extension is the only enclosed structure on the roof.
What would you use as an argument, or do you agree with the city?
The situation is this, an existing 4-story hotel has an occupied roof. The occupied roof was added about six years ago. There are two exterior stairs that lead from the roof and have more than enough egress capacity. The problem is this, the elevator does not extend to the roof, so the owner obtained a permit to extend the elevator shaft to the roof (i.e. a fifth floor).
The elevator work is installed, but now the inspector is requiring that standby power be provided for the elevator per Section 1007.2.1 (2012 IBC), which requires that an elevator be one of the accessible means of egress (because there is now a "floor" that is more than 4 stories above the level of exit discharge), which, in turn, is required to have standby power per Section 1007.4. The cost of adding standby power far exceeds the cost of extending the elevator to the roof, which the owner did not anticipate and was not mentioned during the plan review. If the owner had known this during plan review, he may not have proceeded with the work.
Now I've been hired to draft a code modification that would justify why standby power is not necessary. The owner try to argue that they were altering an existing elevator and that the elevator would not be required to comply with all of the requirements for new construction, just the portion that was altered. The city countered that the shaft extension is actually an "addition," thus requiring full compliance with the IBC. The elevator shaft extension is the only enclosed structure on the roof.
What would you use as an argument, or do you agree with the city?