elevator heat detectors alarm or supervisory

Joined
Sep 16, 2022
Messages
1
Location
Virginia
I noticed that a building, the elevator machine rm and pit and shaft is programmed as a supervisory signal. i don't know if the county plan review approved it or its a mistake by the plan review and contractor. per NFPA 72 a heat detector shall be programmed as a alarm condition correct? can someone tell me if there is a exception in the code to be in supervisory in a building or school. also I notice that they used a nonaddressable device connected to a module and program as a supervisory
 