Elevator Hoistway Door
LGreene
San Miguel de Allende, Mexico
Happy New Year everyone.
I'm wondering if anyone can explain Exception 3 of the section below found in the 2006 edition of the IBC. In other sections of the code where doors are required to be tested per UL1784, the code states the maximum allowable air infiltration, and also states that an artificial bottom seal shall be used during the test. This exception below doesn't state a measurement of how much air is allowed to pass, and says that the test has to be conducted without an artificial bottom seal. Any insight?
Thanks for your help.
- Lori
707.14.1 Elevator lobby. An enclosed elevator lobby shall be provided at each floor where an elevator shaft enclosure connects more than three stories. The lobby shall separate the elevator shaft enclosure doors from each floor by fire partitions equal to the fire-resistance rating of the corridor and the required opening protection. Elevator lobbies shall have at least one means of egress complying with Chapter 10 and other provisions within this code.
1. Enclosed elevator lobbies are not required at the street floor, provided the entire street floor is equipped with an automatic sprinkler system in accordance with Section 903.3.1.1.
2. Elevators not required to be located in a shaft in accordance with Section 707.2 are not required to have enclosed elevator lobbies.
3. Where additional doors are provided at the hoistway opening in accordance with Section 3002.6. Such doors shall be tested in accordance with UL 1784 without an artificial bottom seal.
4. In other than Group I-3, and buildings having occupied floors located more than 75 feet (22 860 mm) above the lowest level of fire department vehicle access, enclosed elevator lobbies are not required where the building is protected by an automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2.
5. Smoke partitions shall be permitted in lieu of fire partitions to separate the elevator lobby at each floor where the building is equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2.
6. Enclosed elevator lobbies are not required where the elevator hoistway is pressurized in accordance with Section 707.14.2
Re: Elevator Hoistway Door
If you have the commentary it explains it,
and says with out the seal the door has to be tighter to meet
ul 1784
You would probably get more action out of this if it were moved to the Commercial Building forum, a little out of place here. Contact one of the mods, jpranch or mmmarvel, above.
JMHO ;)