These guys just don't get it! They called me again this AM wanting to know why they couldn't discharge the elevator pit into the grease interceptor.
Here is my response.What do you think?
From the 2006 IPC,
1003.3 Grease interceptors. Grease interceptors shall comply
with the requirements of Sections 1003.3.1 through 1003.3.5.
1003.3.1 Grease interceptors and automatic grease
removal devices required. A grease interceptor or automatic
grease removal device shall be required to receive the
drainage from fixtures and equipment with grease-laden
waste located in food preparation areas, such as in restaurants,
hotel kitchens, hospitals, school kitchens, bars, factory
cafeterias and clubs. Fixtures and equipment shall
include pot sinks, prerinse sinks; soup kettles or similar
devices; wok stations; floor drains or sinks into which kettles
are drained; automatic hoodwash units and dishwashers
without prerinse sinks. Grease interceptors and automatic
grease removal devices shall receive waste only from fixtures
and equipment that allow fats, oils or grease to be discharged.
The code is specific on what is allowed to be discharged into a grease interceptor and that grease interceptors shall receive waste only from fixtures and equipment that allow fats, oils or grease to be discharged.
This section of the code goes on to define fixtures and equipment. Fixtures and equipment shall include pot sinks, prerinse sinks; soup kettles or similar devices; wok stations; floor drains or sinks into which kettles are drained; automatic hoodwash units and dishwashers without prerinse sinks.
Elevator pits are not included as equipment that is allowed to discharge into a grease interceptor.
Then go to section 1003.4 Oil separators required.
1003.4 Oil separators required. At repair garages, car-washing
facilities, at factories where oily and flammable liquid
wastes are produced and in hydraulic elevator pits, separators
shall be installed into which all oil-bearing, grease-bearing or
flammable wastes shall be discharged before emptying into the
building drainage system or other point of disposal.
Exception: An oil separator is not required in hydraulic elevator
pits where an approved alarm system is installed.
Notice that one is an interceptor (grease) and the other is a separator (oil), two different applications. In my opinion the code is very specific on where grease interceptors are required and where an oil separator is required. Grease interceptors shall only accept grease-laden from fixtures and equipment located in food preparation areas. An oil separator is required where oily and flammable liquid wastes are produced.
Elevator pits must discharge into an oil separator however there is an exception in the code for elevator pits.
Exception: An oil separator is not required in hydraulic elevator
pits where an approved alarm system is installed.
So I stand on my original interpretation that the elevator pit cannot discharge into the grease interceptor. You must either install an oil separator for the elevator pit or install an approved alarm system.
Thanks to all that responded. Also....Darren, thanks for the link.