Re: Emergency egress lighting logs
IFC 2006
604.2.4 Means of egress illumination. Emergency power
shall be provided for means of egress illumination in accordance
with Section 1006.3.
604.4 Operational inspection and testing. Emergency power
systems, including all appurtenant components shall be
inspected and tested under load in accordance with NFPA 110
and NFPA 111.
1006.3 Illumination emergency power. The power supply for
means of egress illumination shall normally be provided by the
premises’ electrical supply.In the event of power supply failure, an emergency electrical
system shall automatically illuminate the following areas:
1. Aisles and unenclosed egress stairways in rooms and
spaces that require two or more means of egress.
2. Corridors, exit enclosures and exit passageways in buildings
required to have two or more exits.
3. Exterior egress components at other than the level of exit
discharge until exit discharge is accomplished for buildings
required to have two or more exits.
4. Interior exit discharge elements, as permitted in Section
1024.1, in buildings required to have two or more exits.
5. Exterior landings, as required by Section 1008.1.5, for
exit discharge doorways in buildings required to have
two or more exits.
The emergency power system shall provide power for a
duration of not less than 90 minutes and shall consist of storage
batteries, unit equipment or an on-site generator. The installation
of the emergency power system shall be in accordance
with Section 2702 of the International Building Code.
Exit signs
1011.5.3 Power source. Exit signs shall be illuminated at
all times. To ensure continued illumination for a duration of
not less than 90 minutes in case of primary power loss, the
sign illumination means shall be connected to an emergency
power system provided from storage batteries, unit equipment
or an on-site generator. The installation of the emergency
power system shall be in accordance with Section
2702 of the International Building Code.
Exception: Approved exit sign illumination means that
provide continuous illumination independent of external
power sources for a duration of not less than 90 minutes,
in case of primary power loss, are not required to be connected
to an emergency electrical system.
Testing is done by a NFPA code just as people are to write on the back of the fire extinguisher tag monthly and test smokes monthly.