Would a small storage space, used for storage only, fit exception #2 in the 2018
IBC 2902.3 ( IPC 403.3, # 2 )? Consider this is a larger building being carved
up into several small storage only uses. There are no public access restrooms
within travel distances.
To me the exception is for public facilities, meaning the space is still required to
have fixtures for the employee who may access the space, even if it is for a short
time.
[P] 2902.3 Employee and public toilet facilities.
For structures and tenant spaces intended for public utilization, customers,
patrons and visitors shall be provided with public toilet facilities. Employees
associated with structures and tenant spaces shall be provided with toilet
facilities. The number of plumbing fixtures located within the required toilet
facilities shall be provided in accordance with Section 2902 for all users. Employee
toilet facilities shall be either separate or combined employee and public toilet
facilities.
Exception: Public toilet facilities shall not be required for:
1. Parking garages where operated without parking attendants.
2. Structures and tenant spaces intended for quick transactions, including takeout,
pickup and drop-off, public access area less than or equal to 300 square feet
(28 m2).
As an extension ( if the answer to question above is "No" ), would the fixtures be
required to be fully accessible? IBC 1109.2 offers an exception for a private
bathroom through a private office to be adaptable but not fully accessible. I don't
see the storage space fitting this exception, and if it is the only fixture it would be
required to serve the entire occupant load per IBC T1004.5, which would negate
the "single occupant" limitation.
1109.2 Toilet and bathing facilities.
Each toilet room and bathing room shall be accessible. Where a floor level is not
required to be connected by an accessible route, the only toilet rooms or bathing
rooms provided within the facility shall not be located on the inaccessible floor. Except
as provided for in Sections 1109.2.2 and 1109.2.3, at least one of each type of fixture,
element, control or dispenser in each accessible toilet room and bathing room shall
be accessible.
Exceptions:
1. Toilet rooms or bathing rooms accessed only through a private office, not for
common or public use and intended for use by a single occupant, shall be permitted
to comply with the specific exceptions in ICC A117.1.
IBC 2902.3 ( IPC 403.3, # 2 )? Consider this is a larger building being carved
up into several small storage only uses. There are no public access restrooms
within travel distances.
To me the exception is for public facilities, meaning the space is still required to
have fixtures for the employee who may access the space, even if it is for a short
time.
[P] 2902.3 Employee and public toilet facilities.
For structures and tenant spaces intended for public utilization, customers,
patrons and visitors shall be provided with public toilet facilities. Employees
associated with structures and tenant spaces shall be provided with toilet
facilities. The number of plumbing fixtures located within the required toilet
facilities shall be provided in accordance with Section 2902 for all users. Employee
toilet facilities shall be either separate or combined employee and public toilet
facilities.
Exception: Public toilet facilities shall not be required for:
1. Parking garages where operated without parking attendants.
2. Structures and tenant spaces intended for quick transactions, including takeout,
pickup and drop-off, public access area less than or equal to 300 square feet
(28 m2).
As an extension ( if the answer to question above is "No" ), would the fixtures be
required to be fully accessible? IBC 1109.2 offers an exception for a private
bathroom through a private office to be adaptable but not fully accessible. I don't
see the storage space fitting this exception, and if it is the only fixture it would be
required to serve the entire occupant load per IBC T1004.5, which would negate
the "single occupant" limitation.
1109.2 Toilet and bathing facilities.
Each toilet room and bathing room shall be accessible. Where a floor level is not
required to be connected by an accessible route, the only toilet rooms or bathing
rooms provided within the facility shall not be located on the inaccessible floor. Except
as provided for in Sections 1109.2.2 and 1109.2.3, at least one of each type of fixture,
element, control or dispenser in each accessible toilet room and bathing room shall
be accessible.
Exceptions:
1. Toilet rooms or bathing rooms accessed only through a private office, not for
common or public use and intended for use by a single occupant, shall be permitted
to comply with the specific exceptions in ICC A117.1.