Mech
REGISTERED
2009 IMC
I am interpreting section 404.2 to say that an enclosed parking garage must have continuous ventilation, 24/7, at a rate of 0.05 cfm / sf and must be capable of increasing to 0.75 cfm / sf. Is this correct?
Is section 404.3 requiring positive pressure in the restrooms to keep any parking garage fumes out? I do not want to go nuts on this, but I want it to be correct.
Thanks!
SECTION 404 ENCLOSED PARKING GARAGES
404.1 Enclosed parking garages. Mechanical ventilation systems for enclosed parking garages shall be permitted to operate intermittently where the system is arranged to operate automatically upon detection of vehicle operation or the presence of occupants by approved automatic detection devices.
404.2 Minimum ventilation. Automatic operation of the system shall not reduce the ventilation airflow rate below 0.05 cfm per square foot (0.00025 m3/s ∙ m2) of the floor area and the system shall be capable of producing a ventilation airflow rate of 0.75 cfm per square foot (0.0038 m3/s ∙ m2) of floor area.
404.3 Occupied spaces accessory to public garages. Connecting offices, waiting rooms, ticket booths and similar uses that are accessory to a public garage shall be maintained at a positive pressure and shall be provided with ventilation in accordance with Section 403.3.
I am interpreting section 404.2 to say that an enclosed parking garage must have continuous ventilation, 24/7, at a rate of 0.05 cfm / sf and must be capable of increasing to 0.75 cfm / sf. Is this correct?
Is section 404.3 requiring positive pressure in the restrooms to keep any parking garage fumes out? I do not want to go nuts on this, but I want it to be correct.
Thanks!
SECTION 404 ENCLOSED PARKING GARAGES
404.1 Enclosed parking garages. Mechanical ventilation systems for enclosed parking garages shall be permitted to operate intermittently where the system is arranged to operate automatically upon detection of vehicle operation or the presence of occupants by approved automatic detection devices.
404.2 Minimum ventilation. Automatic operation of the system shall not reduce the ventilation airflow rate below 0.05 cfm per square foot (0.00025 m3/s ∙ m2) of the floor area and the system shall be capable of producing a ventilation airflow rate of 0.75 cfm per square foot (0.0038 m3/s ∙ m2) of floor area.
404.3 Occupied spaces accessory to public garages. Connecting offices, waiting rooms, ticket booths and similar uses that are accessory to a public garage shall be maintained at a positive pressure and shall be provided with ventilation in accordance with Section 403.3.