• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Equipment Platform - occupant load / egress

Mech

Registered User
Joined
Oct 30, 2009
Messages
1,038
Location
Eastern PA
2006 IBC

Do I calculate an occupancy load for egress from equipment platforms or not since it is unoccupied? Seems to me an unoccupied area would have a zero occupant load.

In my application, I have a 75 ft common path of egress and 200 ft exit access travel distance. Do the 75 ft and 200 ft apply from the most remote part of the equipment platform? From the intersection of the occupied floor / equipment platform?

If you can, please site the code section(s) also.

Thanks in advance.
 
Re: Equipment Platform - occupant load / egress

Sure - what else would you like to know?
 
Re: Equipment Platform - occupant load / egress

06 IBC

Section 502.1 an equipment platform is defined as "An unoccupied, elevated platform used exclusively for mechanical systems or industrial process equipment, including the associated elevated walkways, stairs and ladders necessary to access the platform"

Section 1002.1 means of egress is defined as "A continuous and unobstructed path of vertical and horizontal egress travel from any occupied portion of a building or structure to a public way. A means of egress consists of three separate and distinct parts: the exit access, the exit and the exit discharge."

Do you need more?
 
Top