Exceptions in 2612.6 - Fiber reinforced polymer or fiberglass reinforced polymer

Ryan Schultz

SAWHORSE
Joined
Apr 2, 2012
Messages
283
Location
Madison, WI
Code in question...

Section 2612.6 Exterior use. Fiber reinforced polymer or fiberglass reinforced polymer shall be permitted to be installed on the exterior walls of buildings of any type of construction when such polymers meet the requirements of1. Section 2603.5 and is...

2. fireblocked in accordance with Section 717….

3. The fiber reinforced polymer or the fiberglass reinforced polymer shall be designed for uniform live loads as required in Table 1607.1 as well as for snow loads, wind loads and earthquake loads as specified in Sections 1608, 1609 and 1613, respectively.
Question: From my understanding, if we satisfy exceptions 2612.6.2.1-2612.6.2.4 below, we do not have to comply with the 1-3 requirements outlined in section 2612.6 stated above here. Would this be a correct assumption?

Exceptions:

  • 2. When installed on buildings that are 40 feet (12 190 mm) or less above grade, the fiber reinforced polymer or the fiberglass reinforced polymer shall meet the requirements of Section 1406.2 and shall comply with all of the following conditions:
  • 2.1. Where the fire separation distance is 5 feet (1524 mm) or less, the area of the fiber reinforced polymer or the fiberglass reinforced polymer shall not exceed 10 percent of the wall area. Where the fire separation distance is greater than 5 feet (1524 mm), there shall be no limit on the area of the exterior wall coverage using fiber reinforced polymer or the fiberglass reinforced polymer.
  • 2.2. The fiber reinforced polymer or the fiberglass reinforced polymer shall have a flame spread index of 200 or less. The flame spread index requirement shall not be required for coatings or paints having a thickness of less than 0.036 inch (0.9 mm) that are applied directly to the surface of the fiber reinforced polymer or the fiberglass reinforced polymer.
  • 2.3. Fireblocking complying with Section 717.2.6 shall be installed.
 
It should still be designed for the loads in 3. You don't want a fancy cornice full of snow falling on somebody's head!
 
whoops forgot to include exception 2.4

Stated again, just in case. If we comply with this...

2. When installed on buildings that are 40 feet (12 190 mm) or less above grade, the fiber reinforced polymer or the fiberglass reinforced polymer shall meet the requirements of Section 1406.2 and shall comply with all of the following conditions:2.1. Where the fire separation distance is 5 feet (1524 mm) or less, the area of the fiber reinforced polymer or the fiberglass reinforced polymer shall not exceed 10 percent of the wall area. Where the fire separation distance is greater than 5 feet (1524 mm), there shall be no limit on the area of the exterior wall coverage using fiber reinforced polymer or the fiberglass reinforced polymer.

2.2. The fiber reinforced polymer or the fiberglass reinforced polymer shall have a flame spread index of 200 or less. The flame spread index requirement shall not be required for coatings or paints having a thickness of less than 0.036 inch (0.9 mm) that are applied directly to the surface of the fiber reinforced polymer or the fiberglass reinforced polymer.

2.3. Fireblocking complying with Section 717.2.6 shall be installed.

2.4. The fiber reinforced polymer or the fiberglass reinforced polymer shall be designed for uniform live loads as required in Table 1607.1 as well as for snow loads, wind loads and earthquake loads as specified in Sections 1608, 1609 and 1613, respectively.
We are not required to comply with the following, correct?...

Section 2612.6 Exterior use. Fiber reinforced polymer or fiberglass reinforced polymer shall be permitted to be installed on the exterior walls of buildings of any type of construction when such polymers meet the requirements of1. Section 2603.5 and is...

2. fireblocked in accordance with Section 717….

3. The fiber reinforced polymer or the fiberglass reinforced polymer shall be designed for uniform live loads as required in Table 1607.1 as well as for snow loads, wind loads and earthquake loads as specified in Sections 1608, 1609 and 1613, respectively.
 