I have an existing 2 story grand stair that I do not need for egress requirements. It has a 3" diameter handrail. Per 2012 IEBC
805.9.1 Minimum requirement. Every required exit stairway that is part of the means of egress for any work area and that has three or more risers and is not provided with at least one handrail, or in which the existing handrails are judged to be in danger of collapsing, shall be provided with handrails for the full length of the run of steps on at least one side. All exit stairways with a required egress width of more than 66 inches (1676 mm) shall have handrails on both sides.
805.9.2 Design. Handrails required in accordance with Section 805.9.1 shall be designed and installed in accordance with the provisions of the International Building Code.
If the stair is not required for egress do I need to bring the handrail up to IBC diameter?
805.9.1 Minimum requirement. Every required exit stairway that is part of the means of egress for any work area and that has three or more risers and is not provided with at least one handrail, or in which the existing handrails are judged to be in danger of collapsing, shall be provided with handrails for the full length of the run of steps on at least one side. All exit stairways with a required egress width of more than 66 inches (1676 mm) shall have handrails on both sides.
805.9.2 Design. Handrails required in accordance with Section 805.9.1 shall be designed and installed in accordance with the provisions of the International Building Code.
If the stair is not required for egress do I need to bring the handrail up to IBC diameter?