I have an older, single story, 4,000 square foot existing type VB unsprinklered building (never built to any particular code) that was most recently a bar/restaurant. It is being converted to an office building with an A3 training/meeting area which will make up approximately 500 square feet of the existing 4,000.
The construction will be under the 2006 I-Codes and Chapter 34 for existing since they did not declare the IEBC, only the IBC. In PA they have a choice of one or the other but not both.
Extensive renovations, moving walls, structural repairs in the basement (piers, beams, etc), etc. will be taking place.
There are 3 existing bathrooms, none of which are accessible under the ANSI 117.1 2003 which is what applies in PA.
They will be removing one of the bathrooms and leaving the other 2 in place which will service part of the office are but not any particular office.
They will be installing 2 new bathrooms which will be ANSI 117.1 compliant for a grand total of 4, only half are accessible. The existing 2 that are not accessible are not clustered together.
The DP is trying to declare an occupant load of 40 by taking office space of 4,000 and dividing by 100. He is not taking into consideration that 500 of the 4,000 is already declared A3 with loose chairs as seating which would give us 72 just in that room alone.
1) Can the 2 existing that are not accessible remain without being accessible?
1) How would you treat the occupant load?
My initial opinions are as follows:
1) The 2 existing bathrooms cannot remain without being accessible.
2) The submitted occupant load of 40 is incorrect. He can deduct the bathrooms, basement stairway openings, etc., and recofigure the A3 space for loose tables and chairs to reduce the load otherwise he will have to add bathrooms.
Thanks in advance.
The construction will be under the 2006 I-Codes and Chapter 34 for existing since they did not declare the IEBC, only the IBC. In PA they have a choice of one or the other but not both.
Extensive renovations, moving walls, structural repairs in the basement (piers, beams, etc), etc. will be taking place.
There are 3 existing bathrooms, none of which are accessible under the ANSI 117.1 2003 which is what applies in PA.
They will be removing one of the bathrooms and leaving the other 2 in place which will service part of the office are but not any particular office.
They will be installing 2 new bathrooms which will be ANSI 117.1 compliant for a grand total of 4, only half are accessible. The existing 2 that are not accessible are not clustered together.
The DP is trying to declare an occupant load of 40 by taking office space of 4,000 and dividing by 100. He is not taking into consideration that 500 of the 4,000 is already declared A3 with loose chairs as seating which would give us 72 just in that room alone.
1) Can the 2 existing that are not accessible remain without being accessible?
1) How would you treat the occupant load?
My initial opinions are as follows:
1) The 2 existing bathrooms cannot remain without being accessible.
2) The submitted occupant load of 40 is incorrect. He can deduct the bathrooms, basement stairway openings, etc., and recofigure the A3 space for loose tables and chairs to reduce the load otherwise he will have to add bathrooms.
Thanks in advance.