From the 2009 IFC:
903.6 Existing buildings.
The provisions of this section are
intended to provide a reasonable degree of safety in existing
structures not complying with the minimum requirements of
the International Building Code by requiring installation of an
automatic fire-extinguishing system.
How have you interpreted this requirement? This section is followed by two subparagraphs, 903.6.1 and 903.6.2, which refer to structures that store or manufacture pyroxylin plastic and for Group I-2 structures, respectively.
When it states "this section," is it referring only to the two subparagraphs or all of Section 903? If the latter, then it could be interpreted that any existing building that does not comply with the fire sprinkler installation requirements of the IBC would then be required to retroactively install a system; but I cannot honestly believe that was the intention.
The IFC Code and Commentary is useless in providing any clarification as to the intent and application of this requirement.
903.6 Existing buildings.
The provisions of this section are
intended to provide a reasonable degree of safety in existing
structures not complying with the minimum requirements of
the International Building Code by requiring installation of an
automatic fire-extinguishing system.
How have you interpreted this requirement? This section is followed by two subparagraphs, 903.6.1 and 903.6.2, which refer to structures that store or manufacture pyroxylin plastic and for Group I-2 structures, respectively.
When it states "this section," is it referring only to the two subparagraphs or all of Section 903? If the latter, then it could be interpreted that any existing building that does not comply with the fire sprinkler installation requirements of the IBC would then be required to retroactively install a system; but I cannot honestly believe that was the intention.
The IFC Code and Commentary is useless in providing any clarification as to the intent and application of this requirement.