• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Existing Vending Machine GFCI

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,092
Location
Somewhere Too Hot & Humid
What say you in your state? If you have an old, cord and plug vending machine that has been in the same place for more than 10 years and it needs work, is the electric that supplies it required to be upgraded? The NEC, section 422.51 required vending machines that are directly wired, as well as those that are cord-and-plug connected, are required to be GFCI protected.

If the machine requires maintenance or an upgrade like a new PC board, dollar bill collector or credit card reader, etc., or adding UPS in the machine, is the outlet required to meet the 422.51?
 
That's a tricky one..like the chicken and the egg. If they unplug the machine they can't plug it back in without GFCI protection. Hardwired...not so much.
 
If the building wiring is not altered, no
If the building wiring is repaired or altered, yes
There is no permit required to maintain the machine
 
Interesting.....I think I would go with required, but since there is no permit (cord and plug), it won't happen....

IBC 105.2 Work exempt from permit.

Exemptions from permit requirements of this code shall not be deemed to grant authorization for any work to be done in any manner in violation of the provisions of this code or any other laws or ordinances of this jurisdiction.
 
Perhaps not for us to regulate or require GFCI protection, but, as soon as someone is zapped or injured, everyone is at fault for not providing the protection the code requires.
But, as a means of CYA, we recommend that GFCI protection is put in place when these things are identified.
 
Had't moved it for 10 years, "Wonder if those Cheetos's are still good laying under it?"
 
That's a tricky one..like the chicken and the egg. If they unplug the machine they can't plug it back in without GFCI protection. Hardwired...not so much.
Hardwired...per 2014 NEC (422.51B) you Shall use a GFCI Breaker.
 