Ryan Schultz
SAWHORSE
Per the following, if you have existing wood floor joists within 18" of a Type I hood, you have to replace these joists with non-combustible ones? Seems onerous and not what I have anecdotally seen.
up.codes
507.2.6 Clearances for Type I Hood
A Type I hood shall be installed with a clearance to combustibles of not less than 18 inches (457 mm).
Exception: Clearance shall not be required from gypsum wallboard or 1/2-inch (12.7 mm) or thicker cementitious wallboard attached to noncombustible structures provided that a smooth, cleanable, nonabsorbent and noncombustible material is installed between the hood and the gypsum or cementitious wallboard over an area extending not less than 18 inches (457 mm) in all directions from the hood.

Chapter 5: Exhaust Systems, Mechanical Code 2015 of Wisconsin | UpCodes
UpCodes offers a consolidated resource of construction and building code grouped by jurisdiction

A Type I hood shall be installed with a clearance to combustibles of not less than 18 inches (457 mm).
Exception: Clearance shall not be required from gypsum wallboard or 1/2-inch (12.7 mm) or thicker cementitious wallboard attached to noncombustible structures provided that a smooth, cleanable, nonabsorbent and noncombustible material is installed between the hood and the gypsum or cementitious wallboard over an area extending not less than 18 inches (457 mm) in all directions from the hood.