BayPointArchitect
Sawhorse
Given:
1028.1 General.
Exits shall discharge directly to the exterior of the building. The exit discharge shall be at grade or shall provide a direct path of egress travel to grade. The exit discharge shall not reenter a building. The combined use of Exceptions 1 and 2 shall not exceed 50 percent of the number and minimum width or required capacity of the required exits.
Exceptions:
2. Not more than 50 percent of the number and minimum width or required capacity of the interior exit stairways and ramps is permitted to egress through a vestibule provided that all of the following conditions are met:
2.1. The entire area of the vestibule is separated from areas below by construction conforming to the fire-resistance rating of the interior exit stairway or ramp enclosure.
2.2. The depth from the exterior of the building is not greater than 10 feet and the length is not greater than 30 feet.
2.3. The area is separated from the remainder of the level of exit discharge by a fire partition constructed in accordance with Section 708.
2.4. The area is used only for means of egress and exits directly to the outside.
Questions:
1. How is the depth and length measured for this existing building?
See attached floor plan.
2. If all of the walls surrounding the yellow exit access area are noted as two-hour fire-rated, can this be solved as a horizontal exit?
As always, thanks in advance for your help. Meanwhile, I will see if I can find a code commentary that explains this.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
2018 IBC
Section 1028
EXIT DISCHARGE
Section 1028
EXIT DISCHARGE
1028.1 General.
Exits shall discharge directly to the exterior of the building. The exit discharge shall be at grade or shall provide a direct path of egress travel to grade. The exit discharge shall not reenter a building. The combined use of Exceptions 1 and 2 shall not exceed 50 percent of the number and minimum width or required capacity of the required exits.
Exceptions:
2. Not more than 50 percent of the number and minimum width or required capacity of the interior exit stairways and ramps is permitted to egress through a vestibule provided that all of the following conditions are met:
2.1. The entire area of the vestibule is separated from areas below by construction conforming to the fire-resistance rating of the interior exit stairway or ramp enclosure.
2.2. The depth from the exterior of the building is not greater than 10 feet and the length is not greater than 30 feet.
2.3. The area is separated from the remainder of the level of exit discharge by a fire partition constructed in accordance with Section 708.
2.4. The area is used only for means of egress and exits directly to the outside.
Questions:
1. How is the depth and length measured for this existing building?
See attached floor plan.
2. If all of the walls surrounding the yellow exit access area are noted as two-hour fire-rated, can this be solved as a horizontal exit?
As always, thanks in advance for your help. Meanwhile, I will see if I can find a code commentary that explains this.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner