• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Exit door under stairs

Francis Vineyard

Registered User
Joined
Jan 1, 2010
Messages
3,105
Location
Charlottesville, VA
2 Story office; grade level exterior exit door under stairs of 2nd story; does this violate section 1009.9.4 even if it's protected?

1009.9.4Enclosures under exterior stairways.

There shall be no enclosed usable space under exterior exit stairways unless the space is completely enclosed in 1-hour fire-resistance-rated construction. The open space under exterior stairways shall not be used for any purpose.

Francis

 
Last edited by a moderator:
Does an exit under the exterior stairs considered as used for any purpose? Now come to think of all these exterior stairs that zig-zag from one exit to another; it must be okay.

Can have storage if it's protected; so what is any other purpose?

Francis
 
Exit stair enclosures can be used for normal circulation. They cannot be used for storage, vending machines, smoking areas or other uses.
 
Coug Dad, it's not enclosed!

The section seems to say if you want to use the space then it shall be enclosed a minimum 1-hour protected. But if it's open then you can't use the space at all even if the understair is minimum 1-hour protected; correct?

Thanks for explaining

Francis
 