exit stairs enclosed?
Mr. Inspector
Poconos/eastern PA
A use, B2 constructon, sprinklered, indoor water park. About needing an enclosed stairway to the exit with at least an one hour fire barrier. The stairway connects less than 4 stories ( zero stories is less than 4), does not penetrate a floor. The way the code is writen it looks like they need the enclosed stairway but the commentary only talks about connecting storys and these stairs don't connect stories. The stairs are against a extior foundation wall and go from the ground floor up 8' to an exit door that is to grade (the ground floor is below grade at this point.
1022.1 Enclosures required. Interior exit stairways and interior exit ramps shall be enclosed with fire barriers constructed in accordance with Section 707 or horizontal assemblies constructed in accordance with Section 712, or both. Exit enclosures shall have a fire-resistance rating of not less than 2 hours where connecting four stories or more and not less than 1 hour where connecting less than four stories. The number of stories connected by the exit enclosure shall include any basements but not any mezzanines. Exit enclosures shall have a fire-resistance rating not less than the floor assembly penetrated, but need not exceed 2 hours. Exit enclosures shall lead directly to the exterior of the building or shall be extended to the exterior of the building with an exit passageway conforming to the requirements of Section 1023, except as permitted in Section 1027.1. An exit enclosure shall not be used for any purpose other than means of egress.
1. In all occupancies, other than Group H and I occupancies, a stairway is not required to be enclosed when the stairway serves an occupant load of less than 10 and the stairway complies with either Item 1.1 or 1.2. In all cases, the maximum number of connecting open stories shall not exceed two.
1.1. The stairway is open to not more than one story above its level of exit discharge; or
1.2. The stairway is open to not more than one story below its level of exit discharge.
2. Exits in buildings of Group A-5 where all portions of the means of egress are essentially open to the outside need not be enclosed.
3. Stairways serving and contained within a single residential dwelling unit or sleeping unit in Group R-1, R-2 or R-3 occupancies are not required to be enclosed.
4. Stairways in open parking structures that serve only the parking structure are not required to be enclosed.
5. Stairways in Group I-3 occupancies, as provided for in Section 408.3.8, are not required to be enclosed.
6. Means of egress stairways as required by Sections 410.5.3 and 1015.6.1 are not required to be enclosed.
7. Means of egress stairways from balconies, galleries or press boxes as provided for in Section 1028.5.1 are not required to be enclosed.
Am I missing somthing?